RCC-07-02 Chapter 07 · Design of Footings and Foundations

One-Way and Two-Way (Punching) Shear in Footings

In this chapter (3 topics)
On this page
  1. 1. Introduction to Shear Failure Modes in Footings
  2. 2. One-Way (Wide-Beam) Shear Mechanics & Critical Section at d
  3. 2.1 Critical Section Location (IS 456 Clause 34.2.4.1a)
  4. 2.2 Physical Basis for Distance d
  5. 3. Mathematical Derivation of One-Way Shear Force Vu1 and Stress τv
  6. 3.1 Tributary Shear Area and Factored Shear Force Vu1
  7. 3.2 Nominal One-Way Shear Stress τv1
  8. 4. Permissible One-Way Shear Strength τc
  9. Table 19 Values for Standard Footing Design (pt ≈ 0.20\%--0.35\%)
  10. 5. Two-Way (Punching) Shear Mechanics & Critical Perimeter at d/2
  11. 5.1 Physical Phenomenon of Punching Failure
  12. 5.2 Critical Punching Perimeter b0 (IS 456 Clause 31.6.1)
  13. 6. Mathematical Derivation of Punching Shear Force Vup and Stress τvp
  14. 6.1 Factored Punching Shear Force Vup
  15. 6.2 Nominal Punching Shear Stress τvp
  16. 7. Permissible Two-Way Punching Shear Strength (IS 456 Clause 31.6.3.1)
  17. 7.1 Physical Basis for the ks Factor
  18. Table: Permissible Punching Shear Values τc' = 0.25 √fck
  19. 8. Detailed Engineering Diagrams & Visual Walkthrough
  20. Figure 1: One-Way Shear vs Two-Way Punching Shear Critical Sections
  21. Figure 2: Punching Shear Truncated Pyramid & Aspect Ratio Factor ks
  22. 9. Pre-Calculated Solved Numerical Examples
  23. Problem 1: Complete Shear Verification of a Square Isolated Footing
  24. Problem 2: Punching Shear in a Rectangular Column (Effect of ks)
  25. Problem 3: One-Way Shear in a Sloped Footing with Varying Effective Depth
  26. 10. Comprehensive Comparison Table: One-Way vs Two-Way Shear
  27. 11. Practical Detailing and Common Field Pitfalls
  28. 12. Competitive Examination Traps & Quick Formula Sheet
  29. Common Exam Traps
  30. Master Formula Sheet
  31. 13. Practice Problems
  32. Problem 1 (GATE CE Format - NAT)
  33. Problem 2 (UPSC ESE Format - Multiple Choice)
  34. Problem 3 (State AE / SSC JE Format)

1. Introduction to Shear Failure Modes in Footings

While flexural bending moment dictates the required quantity of bottom tensile reinforcement, the structural thickness (overall depth DD and effective depth dd) of reinforced concrete footings is almost universally governed by shear.

In conventional reinforced concrete design, footings are constructed as broad slabs without transverse shear reinforcement (stirrups or bent-up bars) due to practical placement difficulties and shallow depth. Consequently, the concrete cross-section itself must provide sufficient shear capacity to withstand internal diagonal tension stresses.

Under the action of concentrated downward column thrust and distributed upward net soil reaction quq_u, footings are susceptible to two distinct failure mechanisms:

                      ONE-WAY (BEAM) SHEAR               TWO-WAY (PUNCHING) SHEAR
                        (Wide-Beam Action)               (Punching Failure Cone)
                            Column                                Column
                             │  │                                  │  │
                        ┌────┴──┴────┐                        ┌────┴──┴────┐
                        │    \       │                        │   /    \   │
                        │     \      │                        │  /      \  │
                        └────────────┘                        └────────────┘
                        Critical Section at d              Critical Perimeter at d/2
  1. One-Way (Wide-Beam) Shear:
    • The footing slab behaves like a wide cantilever beam spanning from the column face to the outer edge.
    • A single diagonal shear-tension crack forms across the entire width of the footing slab.
    • Governed by IS 456:2000 Clause 34.2.4.1(a), with the critical plane located at distance dd from the column face.
  2. Two-Way (Punching) Shear:
    • The column thrust punches through the footing slab, causing a truncated pyramid or cone of concrete to push downward through the slab along 45∘45^\circ diagonal tensile failure surfaces.
    • Governed by IS 456:2000 Clause 34.2.4.1(b) and Clause 31.6, with the critical shear perimeter located at distance d/2d/2 all around the column perimeter.

2. One-Way (Wide-Beam) Shear Mechanics & Critical Section at dd

2.1 Critical Section Location (IS 456 Clause 34.2.4.1a)

For one-way shear, the footing is considered as a wide cantilever beam. The critical vertical section across the full width of the footing is taken:

  1. For Footings on Soil:
    • At a distance dd from the face of the column, pedestal, or wall.
    • (Or at distance dd from the critical section for moment, i.e., halfway between centerline and edge for masonry walls, and halfway between column face and gusset plate edge for steel bases).
  2. For Footings Supported on Piles:
    • At a distance of d/2d/2 from the face of the pile, provided the pile diameter or width is ≥1.5d\ge 1.5 d.

2.2 Physical Basis for Distance dd

Diagonal shear-tension cracks typically initiate at the rebar level at an inclination of approximately 45∘45^\circ. Because the concrete within distance dd of the column face is under high biaxial compression due to the downward column thrust, diagonal tension cracking is suppressed in this immediate zone. The first potential shear-compression diagonal tension failure plane forms at distance dd from the column face.


3. Mathematical Derivation of One-Way Shear Force Vu1V_{u1} and Stress τv\tau_v

Consider an isolated rectangular footing of dimensions L×BL \times B supporting a column of cross-section a×ba \times b under factored net upward soil pressure qu=PuL⋅Bq_u = \frac{P_u}{L \cdot B}:

  • Cantilever projection in the long direction: cL=L−a2c_L = \frac{L - a}{2}.
  • Critical section for one-way shear across width BB is at distance dd from the column face.
          ◄───────────────────────── Length L ─────────────────────────►
         ┌──────────────────┬──────────────┬────────────────────────────┐
         │                  │   Column a   │                            │
         │                  │   ┌──────┐   │                            │
         │   (c_L - d)      │ d │      │ d │                            │
         │◄────────────────►│◄─►│      │◄─►│                            │
 Width B │                  │   └──────┘   │                            │
         │                  │              │                            │
         │                  │              │                            │
         └──────────────────┴──────────────┴────────────────────────────┘
          ▲                ▲
          Footing Edge     Critical Section (at distance d from face)
          [── Tributary ──]

3.1 Tributary Shear Area and Factored Shear Force Vu1V_{u1}

The soil reaction acting within distance dd of the column face is transferred directly into the column by inclined compression struts. Only the upward soil pressure acting on the outer cantilever projection beyond the critical plane contributes to the shear force at the critical section:

Tributary Length=cL−d=(L−a2)−d\text{Tributary Length} = c_L - d = \left(\frac{L - a}{2}\right) - d Tributary Area=B×(cL−d)\text{Tributary Area} = B \times (c_L - d)

The factored design shear force Vu1V_{u1} is:

Vu1=qu×B×(cL−d)=qu×B×(L−a2−d)\boxed{V_{u1} = q_u \times B \times (c_L - d) = q_u \times B \times \left(\frac{L - a}{2} - d\right)}

Similarly, for one-way shear in the short direction across length LL:

Vu1,B=qu×L×(cB−d)=qu×L×(B−b2−d)\boxed{V_{u1, B} = q_u \times L \times (c_B - d) = q_u \times L \times \left(\frac{B - b}{2} - d\right)}

3.2 Nominal One-Way Shear Stress τv1\tau_{v1}

τv1=Vu1B⋅d\boxed{\tau_{v1} = \frac{V_{u1}}{B \cdot d}}

Where:

  • Vu1V_{u1} is the factored one-way shear force at the critical section.
  • BB is the lateral width of the footing at the critical section.
  • dd is the effective depth of the footing at the critical section.

4. Permissible One-Way Shear Strength τc\tau_c

According to IS 456:2000 Clause 34.2.4.2, the nominal one-way shear stress τv1\tau_{v1} must not exceed the design shear strength of concrete without shear reinforcement:

τv1≤k⋅τc\boxed{\tau_{v1} \le k \cdot \tau_c}

Where:

  • τc\tau_c is the design shear strength of concrete obtained from IS 456:2000 Table 19, which depends on:
    1. The characteristic cube compressive strength of concrete fckf_{ck}.
    2. The percentage of longitudinal tensile reinforcement pt=100AstB⋅dp_t = \frac{100 A_{st}}{B \cdot d}.
  • kk is the depth factor accounting for size effect in slabs and footings (IS 456 Clause 40.2.1.1):
Overall Footing Depth DD ≤150 mm\le 150\text{ mm} 175 mm175\text{ mm} 200 mm200\text{ mm} 225 mm225\text{ mm} 250 mm250\text{ mm} 275 mm275\text{ mm} ≥300 mm\ge 300\text{ mm}
Depth Factor kk 1.301.30 1.251.25 1.201.20 1.151.15 1.101.10 1.051.05 1.001.00

[!NOTE] Because structural footings have an overall depth DD well exceeding 300 mm300\text{ mm} (D≈450–800 mmD \approx 450\text{--}800\text{ mm}), the depth factor kk is almost universally taken as k=1.00k = 1.00.

Table 19 Values for Standard Footing Design (pt≈0.20%–0.35%p_t \approx 0.20\%\text{--}0.35\%)

Concrete Grade pt=0.15%p_t = 0.15\% pt=0.25%p_t = 0.25\% pt=0.50%p_t = 0.50\% pt=0.75%p_t = 0.75\%
M20 0.28 N/mm20.28\text{ N/mm}^2 0.36 N/mm20.36\text{ N/mm}^2 0.48 N/mm20.48\text{ N/mm}^2 0.56 N/mm20.56\text{ N/mm}^2
M25 0.29 N/mm20.29\text{ N/mm}^2 0.36 N/mm20.36\text{ N/mm}^2 0.49 N/mm20.49\text{ N/mm}^2 0.57 N/mm20.57\text{ N/mm}^2
M30 0.29 N/mm20.29\text{ N/mm}^2 0.37 N/mm20.37\text{ N/mm}^2 0.50 N/mm20.50\text{ N/mm}^2 0.59 N/mm20.59\text{ N/mm}^2
M35 0.29 N/mm20.29\text{ N/mm}^2 0.37 N/mm20.37\text{ N/mm}^2 0.50 N/mm20.50\text{ N/mm}^2 0.60 N/mm20.60\text{ N/mm}^2

Because shear stirrups are omitted in footing slabs, if τv1>τc\tau_{v1} > \tau_c, the effective depth dd must be increased until τv1≤τc\tau_{v1} \le \tau_c.


5. Two-Way (Punching) Shear Mechanics & Critical Perimeter at d/2d/2

5.1 Physical Phenomenon of Punching Failure

When high vertical axial force PuP_u is applied through a column of relatively small footprint (a×ba \times b), high concentrated shear stresses are induced in the concrete slab surrounding the column. Failure occurs when a truncated pyramid or truncated cone of concrete punches downward through the slab.

Because diagonal cracking spreads outward at an angle of roughly 45∘45^\circ, the top of the failure cone has dimensions a×ba \times b at the column base, while the bottom of the failure cone has dimensions (a+2d)×(b+2d)(a + 2d) \times (b + 2d) at the rebar level. The average failure perimeter along which diagonal shear stresses are transmitted occurs at the mid-depth of the effective slab thickness, i.e., at distance d/2d/2 from the column faces.

                           Column Shaft
                             ┌──────┐
                             │  Pu  │
                      ───────┴──────┴───────
                     \   d/2 │      │ d/2   /
                      \◄────►│      │◄────►/  ◄── 45° Punching Shear Plane
                       \     └──────┘     /
                        \                /
                      ───┴──────────────┴───  ◄── Bottom rebar mat
                         ◄─ (a + 2d) ─►

5.2 Critical Punching Perimeter b0b_0 (IS 456 Clause 31.6.1)

The critical section for two-way punching shear is taken as a closed perimeter b0b_0 located at distance d2\frac{d}{2} from the periphery of the column, pedestal, or loaded area:

  1. For a Rectangular Column of dimensions a×ba \times b:
    • The dimensions of the critical perimeter are (a+d)(a + d) and (b+d)(b + d).
    • The total punching perimeter length is: b0=2(a+d)+2(b+d)=2(a+b+2d)\boxed{b_0 = 2(a + d) + 2(b + d) = 2(a + b + 2d)}
  2. For a Square Column (a=ba = b): b0=4(a+d)\boxed{b_0 = 4(a + d)}
  3. For a Circular Column of diameter DcolD_{\text{col}}:
    • The critical section is a concentric circle of diameter (Dcol+d)(D_{\text{col}} + d): b0=π(Dcol+d)\boxed{b_0 = \pi (D_{\text{col}} + d)}

6. Mathematical Derivation of Punching Shear Force VupV_{up} and Stress τvp\tau_{vp}

Consider an isolated footing of plan dimensions L×BL \times B loaded by column factored axial thrust PuP_u with uniform net upward soil pressure qu=PuL⋅Bq_u = \frac{P_u}{L \cdot B}:

  • The area enclosed within the critical punching perimeter is Apunch=(a+d)(b+d)A_{\text{punch}} = (a + d)(b + d).
  • The upward soil pressure acting directly beneath this enclosed area opposes the downward column thrust and pushes up on the punching plug itself.
       ◄────────────────────────── Footing Length L ──────────────────────────►
      ┌────────────────────────────────────────────────────────────────────────┐
      │                                                                        │
      │                  TRIBUTARY SOIL REACTION AREA (V_up)                   │
      │                                                                        │
      │               d/2 ┌──────────────────────────┐ d/2                     │
      │              ◄───►│  Critical Perimeter b0   │◄───►                    │
      │                   │      ┌────────────┐      │                         │
      │                   │      │   Column   │      │                         │
      │                   │      │   (a x b)  │      │                         │
      │                   │      └────────────┘      │                         │
      │                   │                          │                         │
      │                   └──────────────────────────┘                         │
      │                                                                        │
      │                                                                        │
      └────────────────────────────────────────────────────────────────────────┘

6.1 Factored Punching Shear Force VupV_{up}

By vertical equilibrium of the footing slab outside the punching cone:

Vup=Pu−qu⋅(a+d)(b+d)=Pu[1−(a+d)(b+d)L⋅B]\boxed{V_{up} = P_u - q_u \cdot (a + d)(b + d) = P_u \left[1 - \frac{(a + d)(b + d)}{L \cdot B}\right]}

For a circular column:

Vup=Pu−qu⋅[π4(Dcol+d)2]V_{up} = P_u - q_u \cdot \left[\frac{\pi}{4}(D_{\text{col}} + d)^2\right]

6.2 Nominal Punching Shear Stress τvp\tau_{vp}

τvp=Vupb0⋅d\boxed{\tau_{vp} = \frac{V_{up}}{b_0 \cdot d}}

Where:

  • VupV_{up} is the factored punching shear force.
  • b0b_0 is the length of the critical punching perimeter at d/2d/2.
  • dd is the effective depth of the footing slab.

7. Permissible Two-Way Punching Shear Strength (IS 456 Clause 31.6.3.1)

According to IS 456:2000 Clause 31.6.3.1, the nominal two-way shear stress τvp\tau_{vp} must not exceed the permissible shear stress τcp\tau_{cp}:

τvp≤τcp=ks×τc′\boxed{\tau_{vp} \le \tau_{cp} = k_s \times \tau_c'}

Where:

  • τc′\tau_c' is the basic permissible two-way shear strength of concrete: τc′=0.25fck\boxed{\tau_c' = 0.25 \sqrt{f_{ck}}} (with fckf_{ck} in N/mm2\text{N/mm}^2 and τc′\tau_c' in N/mm2\text{N/mm}^2).
  • ksk_s is the aspect ratio modifier: ks=min⁡(0.5+βc, 1.0)\boxed{k_s = \min\left(0.5 + \beta_c, \, 1.0\right)} Where: βc=short side of columnlong side of column=ba≤1.0\beta_c = \frac{\text{short side of column}}{\text{long side of column}} = \frac{b}{a} \le 1.0
   k_s
  1.0 ┼──────────────┌─────────────────────── (k_s = 1.0, Plateau)
      │             /│
      │            / │
      │           /  │   k_s = 0.5 + β_c
      │          /   │
  0.5 ┼─────────┘    │
      │              │
    0 ┴──────────────┴───────────────────────► β_c = b / a
      0             0.5                     1.0 (Square)

7.1 Physical Basis for the ksk_s Factor

In rectangular columns with high aspect ratio (a≫ba \gg b), shear stresses are not distributed uniformly around the perimeter. Shear stresses concentrate heavily near the corners and short faces, while the middle portions of long faces carry significantly less shear. To account for this non-uniform stress concentration and premature corner shear distress:

  • When βc≥0.5\beta_c \ge 0.5 (e.g., square column βc=1.0\beta_c = 1.0, or 400×600 mm400 \times 600\text{ mm} with βc=0.67\beta_c = 0.67): ks=1.0k_s = 1.0.
  • When βc<0.5\beta_c < 0.5 (e.g., blade columns or wall-like columns 200×800 mm200 \times 800\text{ mm} with βc=0.25\beta_c = 0.25): ks=0.5+0.25=0.75k_s = 0.5 + 0.25 = 0.75, reducing permissible punching shear strength by 25%25\%!

Table: Permissible Punching Shear Values τc′=0.25fck\tau_c' = 0.25 \sqrt{f_{ck}}

Concrete Grade Characteristic Strength fckf_{ck} Basic Permissible τc′=0.25fck\tau_c' = 0.25 \sqrt{f_{ck}} Permissible for Square Col (ks=1.0k_s = 1.0)
M20 20 N/mm220\text{ N/mm}^2 1.118 N/mm21.118\text{ N/mm}^2 1.12 N/mm21.12\text{ N/mm}^2
M25 25 N/mm225\text{ N/mm}^2 1.250 N/mm21.250\text{ N/mm}^2 1.25 N/mm21.25\text{ N/mm}^2
M30 30 N/mm230\text{ N/mm}^2 1.369 N/mm21.369\text{ N/mm}^2 1.37 N/mm21.37\text{ N/mm}^2
M35 35 N/mm235\text{ N/mm}^2 1.479 N/mm21.479\text{ N/mm}^2 1.48 N/mm21.48\text{ N/mm}^2
M40 40 N/mm240\text{ N/mm}^2 1.581 N/mm21.581\text{ N/mm}^2 1.58 N/mm21.58\text{ N/mm}^2

8. Detailed Engineering Diagrams & Visual Walkthrough

Figure 1: One-Way Shear vs Two-Way Punching Shear Critical Sections

The diagram below illustrates the plan and elevation layout of both shear modes, showing the critical plane for one-way shear at distance dd and the critical perimeter for two-way punching shear at distance d/2d/2.

Footing Shear Critical Sections One-Way vs Two-Way

Figure 2: Punching Shear Truncated Pyramid & Aspect Ratio Factor ksk_s

The diagram below details the 3D truncated punching failure cone flaring at 45∘45^\circ, the plot of ks=min⁡(0.5+βc,1.0)k_s = \min(0.5 + \beta_c, 1.0) versus column aspect ratio βc\beta_c, and a complete comparison table of shear criteria.

Punching Shear Truncated Pyramid and Shear Capacity Mechanics

9. Pre-Calculated Solved Numerical Examples

Problem 1: Complete Shear Verification of a Square Isolated Footing

Statement: A square isolated footing of plan dimensions 2.50 m×2.50 m2.50\text{ m} \times 2.50\text{ m} supports a square column of size 400 mm×400 mm400\text{ mm} \times 400\text{ mm}. The column transmits a factored axial load Pu=1600 kNP_u = 1600\text{ kN}. The materials used are concrete M25 (fck=25 N/mm2f_{ck} = 25\text{ N/mm}^2) and steel Fe 415 (fy=415 N/mm2f_y = 415\text{ N/mm}^2). The footing slab has an overall depth D=600 mmD = 600\text{ mm} and an effective depth d=520 mmd = 520\text{ mm}. Tensile reinforcement provided is pt=0.25%p_t = 0.25\%, corresponding to a permissible shear strength τc=0.36 N/mm2\tau_c = 0.36\text{ N/mm}^2 from IS 456 Table 19. Verify the structural adequacy of the footing against:

  1. Two-way (punching) shear per Clause 31.6.3.
  2. One-way (beam) shear per Clause 34.2.4.

Solution:

Step 1: Factored Net Upward Soil Reaction quq_u

  • Plan area A=2.50×2.50=6.25 m2A = 2.50 \times 2.50 = 6.25\text{ m}^2
  • Upward soil pressure: qu=PuA=16006.25=256.00 kN/m2 (kPa)=0.256 N/mm2q_u = \frac{P_u}{A} = \frac{1600}{6.25} = 256.00\text{ kN/m}^2\text{ (kPa)} = 0.256\text{ N/mm}^2

Step 2: Two-Way (Punching) Shear Check

  • Critical perimeter is located at d2=5202=260 mm\frac{d}{2} = \frac{520}{2} = 260\text{ mm} from the column face.
  • Side of critical square perimeter: a′=a+d=400+520=920 mm=0.92 ma' = a + d = 400 + 520 = 920\text{ mm} = 0.92\text{ m}
  • Critical perimeter length: b0=4×a′=4×920=3680 mmb_0 = 4 \times a' = 4 \times 920 = 3680\text{ mm}
  • Area enclosed within critical perimeter: Apunch=(a′)2=(0.92)2=0.8464 m2A_{\text{punch}} = (a')^2 = (0.92)^2 = 0.8464\text{ m}^2
  • Factored punching shear force: Vup=Pu−qu×Apunch=1600−256.00×0.8464=1600−216.68=1383.32 kNV_{up} = P_u - q_u \times A_{\text{punch}} = 1600 - 256.00 \times 0.8464 = 1600 - 216.68 = 1383.32\text{ kN}
  • Nominal punching shear stress: τvp=Vup×103b0⋅d=1383.32×1033680×520=1,383,3201,913,600=0.7229 N/mm2\tau_{vp} = \frac{V_{up} \times 10^3}{b_0 \cdot d} = \frac{1383.32 \times 10^3}{3680 \times 520} = \frac{1,383,320}{1,913,600} = 0.7229\text{ N/mm}^2
  • Permissible two-way shear stress: βc=400400=1.0  ⟹  ks=min⁡(0.5+1.0,1.0)=1.0\beta_c = \frac{400}{400} = 1.0 \implies k_s = \min(0.5 + 1.0, 1.0) = 1.0 τcp=ks×(0.25fck)=1.0×0.2525=1.0×0.25×5=1.25 N/mm2\tau_{cp} = k_s \times (0.25 \sqrt{f_{ck}}) = 1.0 \times 0.25 \sqrt{25} = 1.0 \times 0.25 \times 5 = 1.25\text{ N/mm}^2
  • Safety evaluation: τvp=0.7229 N/mm2≤τcp=1.25 N/mm2(SAFE, Demand/Capacity=0.578)\tau_{vp} = 0.7229\text{ N/mm}^2 \le \tau_{cp} = 1.25\text{ N/mm}^2 \quad (\mathbf{SAFE},\text{ Demand/Capacity} = 0.578)

Step 3: One-Way (Wide-Beam) Shear Check

  • Cantilever projection from column face: c=L−a2=2500−4002=1050 mm=1.05 mc = \frac{L - a}{2} = \frac{2500 - 400}{2} = 1050\text{ mm} = 1.05\text{ m}
  • Distance from critical section (at distance d=520 mmd = 520\text{ mm}) to footing edge: c−d=1050−520=530 mm=0.53 mc - d = 1050 - 520 = 530\text{ mm} = 0.53\text{ m}
  • Factored one-way shear force on tributary strip (B=2.50 mB = 2.50\text{ m}): Vu1=qu×B×(c−d)=256.00×2.50×0.53=339.20 kNV_{u1} = q_u \times B \times (c - d) = 256.00 \times 2.50 \times 0.53 = 339.20\text{ kN}
  • Nominal one-way shear stress: τv1=Vu1×103B⋅d=339.20×1032500×520=339,2001,300,000=0.2609 N/mm2\tau_{v1} = \frac{V_{u1} \times 10^3}{B \cdot d} = \frac{339.20 \times 10^3}{2500 \times 520} = \frac{339,200}{1,300,000} = 0.2609\text{ N/mm}^2
  • Permissible one-way shear stress:
    • For D=600 mm≥300 mmD = 600\text{ mm} \ge 300\text{ mm}, k=1.0k = 1.0.
    • From Table 19 for M25 and pt=0.25%p_t = 0.25\%, τc=0.36 N/mm2\tau_c = 0.36\text{ N/mm}^2.
  • Safety evaluation: τv1=0.2609 N/mm2≤τc=0.36 N/mm2(SAFE, Demand/Capacity=0.725)\tau_{v1} = 0.2609\text{ N/mm}^2 \le \tau_c = 0.36\text{ N/mm}^2 \quad (\mathbf{SAFE},\text{ Demand/Capacity} = 0.725)

Conclusion: The footing slab effective depth d=520 mmd = 520\text{ mm} (D=600 mmD = 600\text{ mm}) is completely adequate in both punching shear and one-way shear.


Problem 2: Punching Shear in a Rectangular Column (Effect of ksk_s)

Statement: A rectangular column of size 300 mm×600 mm300\text{ mm} \times 600\text{ mm} carries a factored axial load Pu=2000 kNP_u = 2000\text{ kN}. The column is supported on a rectangular isolated footing of size 3.20 m×2.40 m3.20\text{ m} \times 2.40\text{ m}. Concrete grade is M30 (fck=30 N/mm2f_{ck} = 30\text{ N/mm}^2) and steel Fe 500. The footing has an effective depth d=550 mmd = 550\text{ mm}.

  1. Evaluate the column aspect ratio βc\beta_c and the reduction factor ksk_s.
  2. Calculate the critical punching perimeter b0b_0 and factored punching shear force VupV_{up}.
  3. Check the safety of the footing against two-way punching shear per IS 456 Clause 31.6.3.

Solution:

Step 1: Upward Soil Reaction quq_u

  • Plan area A=3.20×2.40=7.68 m2A = 3.20 \times 2.40 = 7.68\text{ m}^2
  • Net factored upward soil reaction: qu=PuA=20007.68=260.42 kPa=0.26042 N/mm2q_u = \frac{P_u}{A} = \frac{2000}{7.68} = 260.42\text{ kPa} = 0.26042\text{ N/mm}^2

Step 2: Evaluation of Aspect Ratio Factor ksk_s

  • Short side of column b=300 mmb = 300\text{ mm}, Long side a=600 mma = 600\text{ mm}
βc=ba=300600=0.50\beta_c = \frac{b}{a} = \frac{300}{600} = 0.50 ks=min⁡(0.5+βc, 1.0)=min⁡(0.5+0.50, 1.0)=1.00k_s = \min(0.5 + \beta_c, \, 1.0) = \min(0.5 + 0.50, \, 1.0) = 1.00

Step 3: Critical Punching Perimeter b0b_0

Critical section is at d2=5502=275 mm\frac{d}{2} = \frac{550}{2} = 275\text{ mm} from all four column faces:

  • Length of critical section: a′=a+d=600+550=1150 mm=1.15 ma' = a + d = 600 + 550 = 1150\text{ mm} = 1.15\text{ m}
  • Width of critical section: b′=b+d=300+550=850 mm=0.85 mb' = b + d = 300 + 550 = 850\text{ mm} = 0.85\text{ m}
  • Critical perimeter: b0=2(a′+b′)=2(1150+850)=2(2000)=4000 mmb_0 = 2(a' + b') = 2(1150 + 850) = 2(2000) = 4000\text{ mm}

Step 4: Factored Punching Shear Force VupV_{up}

  • Enclosed area: Apunch=a′×b′=1.15×0.85=0.9775 m2A_{\text{punch}} = a' \times b' = 1.15 \times 0.85 = 0.9775\text{ m}^2
  • Factored shear force: Vup=Pu−qu×Apunch=2000−260.42×0.9775=2000−254.56=1745.44 kNV_{up} = P_u - q_u \times A_{\text{punch}} = 2000 - 260.42 \times 0.9775 = 2000 - 254.56 = 1745.44\text{ kN}

Step 5: Nominal Punching Shear Stress τvp\tau_{vp}

τvp=Vup×103b0⋅d=1745.44×1034000×550=1,745,4402,200,000=0.7934 N/mm2\tau_{vp} = \frac{V_{up} \times 10^3}{b_0 \cdot d} = \frac{1745.44 \times 10^3}{4000 \times 550} = \frac{1,745,440}{2,200,000} = 0.7934\text{ N/mm}^2

Step 6: Permissible Punching Shear Strength τcp\tau_{cp}

For M30 concrete:

τc′=0.25fck=0.2530=0.25×5.4772=1.3693 N/mm2\tau_c' = 0.25 \sqrt{f_{ck}} = 0.25 \sqrt{30} = 0.25 \times 5.4772 = 1.3693\text{ N/mm}^2 τcp=ks×τc′=1.00×1.3693=1.3693 N/mm2\tau_{cp} = k_s \times \tau_c' = 1.00 \times 1.3693 = 1.3693\text{ N/mm}^2

Step 7: Safety Verification

τvp=0.7934 N/mm2≤τcp=1.3693 N/mm2(SAFE)\tau_{vp} = 0.7934\text{ N/mm}^2 \le \tau_{cp} = 1.3693\text{ N/mm}^2 \quad (\mathbf{SAFE}) Demand-to-Capacity Ratio=0.79341.3693=0.579≤1.0\text{Demand-to-Capacity Ratio} = \frac{0.7934}{1.3693} = 0.579 \le 1.0

[!TIP] Notice that if the column were a wall-like pier of 200 mm×800 mm200\text{ mm} \times 800\text{ mm} (βc=0.25\beta_c = 0.25), ks=0.5+0.25=0.75k_s = 0.5 + 0.25 = 0.75, reducing τcp\tau_{cp} to 0.75×1.3693=1.027 N/mm20.75 \times 1.3693 = 1.027\text{ N/mm}^2.


Problem 3: One-Way Shear in a Sloped Footing with Varying Effective Depth

Statement: A square sloped footing of size 2.40 m×2.40 m2.40\text{ m} \times 2.40\text{ m} supports a column 400 mm×400 mm400\text{ mm} \times 400\text{ mm} carrying a factored axial load Pu=1200 kNP_u = 1200\text{ kN}. The footing slab is sloped uniformly from the column face to the outer edge:

  • Overall depth at column face: Dface=650 mmD_{\text{face}} = 650\text{ mm} (effective depth dface=580 mmd_{\text{face}} = 580\text{ mm}).
  • Overall depth at edge: Dedge=200 mmD_{\text{edge}} = 200\text{ mm} (effective depth dedge=130 mmd_{\text{edge}} = 130\text{ mm}).
  • Cantilever projection from column face: c=2400−4002=1000 mmc = \frac{2400 - 400}{2} = 1000\text{ mm}. Given concrete M25 and pt=0.20%p_t = 0.20\% (τc=0.33 N/mm2\tau_c = 0.33\text{ N/mm}^2), determine:
  1. The exact location of the critical section for one-way shear and the effective depth dcritd_{\text{crit}} at that section.
  2. The nominal one-way shear stress τv\tau_v and verify safety against shear failure.

Solution:

Step 1: Net Factored Upward Soil Pressure quq_u

A=2.40×2.40=5.76 m2A = 2.40 \times 2.40 = 5.76\text{ m}^2 qu=PuA=12005.76=208.33 kPa=0.20833 N/mm2q_u = \frac{P_u}{A} = \frac{1200}{5.76} = 208.33\text{ kPa} = 0.20833\text{ N/mm}^2

Step 2: Location of Critical Section in Sloped Footing

In a prismatic footing, the critical section is at distance dd from the column face. In a sloped footing, the depth d(x)d(x) decreases linearly with distance xx from the column face:

d(x)=dface−(xc)(dface−dedge)d(x) = d_{\text{face}} - \left(\frac{x}{c}\right)(d_{\text{face}} - d_{\text{edge}})

Where c=1000 mm,dface=580 mm,dedge=130 mmc = 1000\text{ mm}, d_{\text{face}} = 580\text{ mm}, d_{\text{edge}} = 130\text{ mm}.

Slope s=dface−dedgec=580−1301000=4501000=0.45\text{Slope } s = \frac{d_{\text{face}} - d_{\text{edge}}}{c} = \frac{580 - 130}{1000} = \frac{450}{1000} = 0.45 d(x)=580−0.45xd(x) = 580 - 0.45 x

The critical section occurs where the distance xx from the column face equals the local effective depth d(x)d(x):

xcrit=d(xcrit)=580−0.45xcritx_{\text{crit}} = d(x_{\text{crit}}) = 580 - 0.45 x_{\text{crit}} xcrit(1+0.45)=580  ⟹  1.45xcrit=580x_{\text{crit}} (1 + 0.45) = 580 \implies 1.45 x_{\text{crit}} = 580 xcrit=5801.45=400.0 mm\boxed{x_{\text{crit}} = \frac{580}{1.45} = 400.0\text{ mm}} dcrit=400.0 mm\boxed{d_{\text{crit}} = 400.0\text{ mm}}

Step 3: Factored Shear Force Vu1V_{u1} at Critical Section

Tributary length beyond xcrit=400 mmx_{\text{crit}} = 400\text{ mm}:

Length=c−xcrit=1000−400=600 mm=0.60 m\text{Length} = c - x_{\text{crit}} = 1000 - 400 = 600\text{ mm} = 0.60\text{ m}

Factored shear force across width B=2.40 mB = 2.40\text{ m}:

Vu1=qu×B×(c−xcrit)=208.33×2.40×0.60=300.00 kNV_{u1} = q_u \times B \times (c - x_{\text{crit}}) = 208.33 \times 2.40 \times 0.60 = 300.00\text{ kN}

Step 4: Nominal Shear Stress τv\tau_v

τv=Vu1×103B⋅dcrit=300.00×1032400×400=300,000960,000=0.3125 N/mm2\tau_v = \frac{V_{u1} \times 10^3}{B \cdot d_{\text{crit}}} = \frac{300.00 \times 10^3}{2400 \times 400} = \frac{300,000}{960,000} = 0.3125\text{ N/mm}^2

Step 5: Permissible Shear Stress Check

From IS 456 Table 19 for M25 concrete and pt=0.20%p_t = 0.20\%:

τc=0.33 N/mm2\tau_c = 0.33\text{ N/mm}^2

Since dcrit=400 mm>300 mmd_{\text{crit}} = 400\text{ mm} > 300\text{ mm}, k=1.0k = 1.0.

τv=0.3125 N/mm2≤τc=0.33 N/mm2(SAFE)\tau_v = 0.3125\text{ N/mm}^2 \le \tau_c = 0.33\text{ N/mm}^2 \quad (\mathbf{SAFE})

[!WARNING] If the engineer mistakenly used the full depth at the column face (dface=580 mmd_{\text{face}} = 580\text{ mm}), the calculated nominal shear stress would be τv=300×1032400×580=0.216 N/mm2\tau_v = \frac{300 \times 10^3}{2400 \times 580} = 0.216\text{ N/mm}^2, hiding a 45%45\% stress underestimation! Always calculate the local depth dcritd_{\text{crit}} at the critical section in sloped footings.


10. Comprehensive Comparison Table: One-Way vs Two-Way Shear

Feature / Criteria One-Way (Wide-Beam) Shear Two-Way (Punching) Shear
Physical Mechanism Diagonal tension crack across full width Truncated 45∘45^\circ pyramid / cone punch-through
Governing Code Clause IS 456 Clause 34.2.4.1(a) IS 456 Clause 34.2.4.1(b) & Clause 31.6
Critical Section Location At distance dd from column face At distance d/2d/2 from column perimeter
Location for Pile Caps Distance d/2d/2 from pile face Distance d/2d/2 from column perimeter
Critical Section Geometry Straight vertical plane of width BB Closed perimeter b0=2(a+b+2d)b_0 = 2(a + b + 2d)
Factored Shear Force Vu1=qu⋅B⋅(c−d)V_{u1} = q_u \cdot B \cdot (c - d) Vup=Pu−qu(a+d)(b+d)V_{up} = P_u - q_u (a + d)(b + d)
Nominal Stress Expression τv1=Vu1B⋅d\tau_{v1} = \frac{V_{u1}}{B \cdot d} τvp=Vupb0⋅d\tau_{vp} = \frac{V_{up}}{b_0 \cdot d}
Permissible Shear Stress τc\tau_c from Table 19 (fck,ptf_{ck}, p_t) τcp=ks(0.25fck)\tau_{cp} = k_s (0.25 \sqrt{f_{ck}})
Aspect Ratio Modification None ks=min⁡(0.5+βc,1.0)k_s = \min(0.5 + \beta_c, 1.0)
Shear Reinforcement Never provided in pad footings; depth governs Occasionally provided in flat slabs; rare in footings
Governing Nature Governs rectangular footings with large L/BL/B Governs depth in almost all square footings

11. Practical Detailing and Common Field Pitfalls

  1. Forgetting to Deduct Upward Soil Pressure from VupV_{up}:
    • In computing punching shear force, designers sometimes use the full column load PuP_u without subtracting the upward soil reaction within the critical perimeter qu(a+d)(b+d)q_u (a+d)(b+d).
    • While conservative, on large footings with deep sections, this adds 10–20%10\text{--}20\% unnecessary thickness.
  2. The Sloped Footing Critical Depth Trap:
    • As demonstrated in Problem 3, in sloped footings the effective depth decreases rapidly away from the column. The critical section for one-way shear occurs at dcrit<dfaced_{\text{crit}} < d_{\text{face}}. Always check shear at the reduced depth!
  3. Omitting Shear Verification in Pile Caps:
    • In pile caps supporting heavy column loads, one-way shear and punching shear across individual pile clusters are critical. Per Clause 34.2.4.1, the one-way shear plane for pile caps is at d/2d/2 from the pile face, not dd!
  4. Shear Reinforcement Restrictions:
    • If a footing depth is severely constrained by site conditions (high water table or shallow rock) and fails in shear, shear stirrups or structural shear heads may be used per Clause 31.6.3. However, standard practice strongly favors increasing concrete depth DD over adding congested shear stirrups in footings.

12. Competitive Examination Traps & Quick Formula Sheet

Common Exam Traps

  1. Critical Section Distances:
    • Bending Moment: At column face.
    • One-Way Shear: At distance dd from column face.
    • Two-Way Punching Shear: At distance d/2d/2 from column perimeter.
    • Pile Cap One-Way Shear: At distance d/2d/2 from pile face.
  2. Formula for Permissible Punching Shear:
    • τc=0.25fck\tau_c = \mathbf{0.25 \sqrt{f_{ck}}}, NOT 0.16fck0.16 \sqrt{f_{ck}} (which is working stress).
    • In Limit State Method, the factor is strictly 0.250.25.
  3. Aspect Ratio Factor ksk_s Limits:
    • ks=min⁡(0.5+βc,1.0)k_s = \min(0.5 + \beta_c, 1.0), where βc=short sidelong side≤1.0\beta_c = \frac{\text{short side}}{\text{long side}} \le 1.0.
    • ksk_s is never greater than 1.01.0 and never less than 0.50.5!
  4. Punching Perimeter b0b_0 for Circular Columns:
    • For a circular column of diameter DcolD_{\text{col}}, b0=π(Dcol+d)b_0 = \mathbf{\pi (D_{\text{col}} + d)}.

Master Formula Sheet

Vu1=qu⋅B⋅(L−a2−d)\boxed{V_{u1} = q_u \cdot B \cdot \left(\frac{L - a}{2} - d\right)} τv1=Vu1B⋅d≤k⋅τc(Table 19)\boxed{\tau_{v1} = \frac{V_{u1}}{B \cdot d} \le k \cdot \tau_c \quad (\text{Table 19})} b0=2(a+d)+2(b+d)=2(a+b+2d)\boxed{b_0 = 2(a + d) + 2(b + d) = 2(a + b + 2d)} Vup=Pu−qu(a+d)(b+d)\boxed{V_{up} = P_u - q_u (a + d)(b + d)} τvp=Vupb0⋅d≤ks(0.25fck)\boxed{\tau_{vp} = \frac{V_{up}}{b_0 \cdot d} \le k_s \left(0.25 \sqrt{f_{ck}}\right)} ks=min⁡(0.5+ba, 1.0)\boxed{k_s = \min\left(0.5 + \frac{b}{a}, \, 1.0\right)}

13. Practice Problems

Problem 1 (GATE CE Format - NAT)

A square footing of size 3.0 m×3.0 m3.0\text{ m} \times 3.0\text{ m} supports a square column of size 500 mm×500 mm500\text{ mm} \times 500\text{ mm}. The column carries a factored axial load Pu=1800 kNP_u = 1800\text{ kN}. The effective depth of the footing is d=500 mmd = 500\text{ mm}. The factored two-way punching shear force VupV_{up} acting on the critical section is ________ kN\text{kN} (round off to the nearest integer). (Calculation: A=3.0×3.0=9.0 m2A = 3.0 \times 3.0 = 9.0\text{ m}^2. qu=1800/9.0=200 kPaq_u = 1800 / 9.0 = 200\text{ kPa}. Critical section size =a+d=0.5+0.5=1.0 m= a + d = 0.5 + 0.5 = 1.0\text{ m}. Area enclosed =1.0×1.0=1.0 m2= 1.0 \times 1.0 = 1.0\text{ m}^2. Vup=Pu−qu×1.0=1800−200×1.0=1600 kNV_{up} = P_u - q_u \times 1.0 = 1800 - 200 \times 1.0 = 1600\text{ kN}. Answer: 16001600)

Problem 2 (UPSC ESE Format - Multiple Choice)

Consider the following statements regarding the shear design of isolated RCC footings as per IS 456:2000:

  1. The critical section for two-way shear is located at distance dd from the column face.
  2. The permissible shear stress in two-way shear is given by ks×0.25fckk_s \times 0.25 \sqrt{f_{ck}}.
  3. For a rectangular column with aspect ratio b/a=0.25b/a = 0.25, the value of ksk_s is 0.750.75.
  4. The critical section for one-way shear in a pile cap is located at distance d/2d/2 from the face of the pile.

Which of the above statements are correct?

  • (A) 1 and 2 only
  • (B) 2, 3 and 4 only
  • (C) 1, 3 and 4 only
  • (D) 1, 2, 3 and 4 (Answer: (B) 2, 3 and 4 only. Statement 1 is incorrect because critical section for two-way shear is at d/2d/2, not dd.)

Problem 3 (State AE / SSC JE Format)

For a circular column of diameter 400 mm400\text{ mm} supported on an isolated footing of effective depth d=600 mmd = 600\text{ mm}, what is the length of the critical punching shear perimeter b0b_0?

  • (A) 1000 mm1000\text{ mm}
  • (B) 2200 mm2200\text{ mm}
  • (C) 3142 mm3142\text{ mm}
  • (D) 6283 mm6283\text{ mm} (Calculation: b0=π(Dcol+d)=π(400+600)=π×1000=3141.59 mm≈3142 mmb_0 = \pi (D_{\text{col}} + d) = \pi (400 + 600) = \pi \times 1000 = 3141.59\text{ mm} \approx 3142\text{ mm}. Answer: (C))